I have a breaker tripping and can't seem to figure out whats causing it. When ever we have a power outage, one breaker powering an out building trips, I will start @ the utility and walk you down stream to give the whole picture. Utility is 300 KVA MV-480/277 and is feed by 10 sets of 600MCM to a 4000A switchboard, we are then feeding a distribution panel with a 800 amp breaker. Out of this we are coming off a 125 amp breaker feeding a 75 KVA trans 480/208/120 feeding the load center in the building.The 125 amp breaker is the one tripping. Under full load it has 63.5 amps on A phase and 53.5 on B phase and about 8 amps on the neutral. What am I missing?