The only reason the EGC is undersized is that it was initially (and correctly) sized for the OCPD, then a choice was made to increase the size of the ungrounded (phase) conductors, which brought 250.122(B) into play. The EGC is undersized for the upsized phase conductors. But those conductors can support a higher rated OCPD, which might possibly call for the same size EGC as was originally installed. In this case, the phase conductors will not have to be declared to have been ?increased in size,? and possibly the EGC will work as is.
Example:
? Calculated load = 120 amps.
? Selected conductor size = #1 copper (ampacity 130).
? Selected OCPD rating = 125 amps.
? Corresponding EGC size = #6 copper.
? Now someone raises the concern over voltage drop. It is decided to increase the phase conductor to #2/0 (ampacity 175).
? The EGC is required to be increased in size in proportion to the increase from #1 to #2/0 (I won?t do the math, since it doesn?t matter to my example). But they didn?t change the EGC.
? The wires actually pulled are #2/0 for the phase conductors and #6 for the EGC.
? At present, you have a violation of 250.122(B).
? Proposed corrective action: Change the OCPD from 125 amps to 175 amps.
? You now have a match between the ampacity of the conductors and the rating of the OCPD. Therefore, the phase conductors are not ?increased in size.? Therefore, the correct EGC is the one that corresponds to the 175 amp OCPD. That is the same #6 that was originally pulled.
? QED.
This will not work in all circumstances. For example, if the feeder in question is supplying a panelboard that is rated for 125 amps, then you cannot use a 175 amp OCPD at the origin of that feeder.