- Massachusetts
The thing that "securely fastens" is referenced to the "tubing termination", not the "termination point".
Only a "tubing termination" is included in the list with outlet box, junction box, device box, cabinet and conduit body.
Again, I believe a "tubing termination" is a two word term. I believe it means a fitting or assembly that is listed for the conductors to emerge from the end of the raceway.
A coupling is not listed for conductors to emerge from, nor is a "go-from" coupling. Therefore, even though two different types of raceway may end in a "go-from" coupling, no termination can occur.
Al, IMO RMC is outside the scope of Article 358 so it cannot recognize or apply to anything beyond the transition from EMT. The code article as well as the EMT has terminated at the transition.