2 question for 70E

Status
Not open for further replies.

memyselfandI

Senior Member
As per NFPA 70E 205.2 where it says that if a one line diagram is provided it must be maintained, is it a requirement to have one even if one is not developed and if it isn't required how does 120.2(F)(1)(a) come into play?
 
As per NFPA 70E 205.2 where it says that if a one line diagram is provided it must be maintained, is it a requirement to have one even if one is not developed and if it isn't required how does 120.2(F)(1)(a) come into play?
The 100 group of articles deals with creating a safe work environment.
The 200 group of articles deals with maintaining a safe work environment.

How can you work safely in a facility if you don't know where equipment is fed from? Can this be done with a riser diagram instead of a one-line? Of course, it can. Can it be done with panels schedules only? I do not believe so when more than a few panels are involved.
 