Does anyone know where i can find information on penetrating a nema 3R inclosure.I have a 3r box i want to install as a feed threw pull box,But i need to come in the bottom and out the top.It's a 18 by 18 by 6 with no factory k.o's

Thank You,Colin Chisholm
Stafford Electric.
 

iwire

Moderator
Staff member
Location
Massachusetts
Punch a hole in the top and use a fitting listed to seal water out, that might be as fancy as a Myers hub or as simple as a sealing o-ring.
 

cadpoint

Senior Member
Location
Durham, NC
I might be missing exactly what your asking, 3R enclosures don't usually come with any prepunched KO's due to their rating...

If you coming out the top you need a myers hub. Now you got me thinking if it required also out the sides as well ... :)

One can look at these two sites to get some other ideas :

Hoffman

or

DDB (which is a quite more varied)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
All of the 3R disconnects and panel enclosures that I have seen have prepunched KOs. I don't think I have ever seen a 3R pull box.
 