THHN wire left exposed
Halfcrazy
New member
Ok as an electrician I have always believed THHN wire could not be run in walls etc. Now I am being asked for a code reference stating THHN can not be run inside residential walls without protection. Can anyone point me to the proper place in the 2011 book?
Welcome to the forum.:)
Check out 310.10 in the 2011 NEC.
310.10 Uses Permitted. The conductors described in
310.104 shall be permitted for use in any of the wiring
methods covered in Chapter 3 and as specified in their
respective tables or as permitted elsewhere in this Code.
Single conductor THHN installed in a wall is not part of a recognized wiring method covered in Chapter 3.
Chris
What brought you to this way of thinking??
Cavie, did you see the word NOT?
I was brought up thinking the same way. THHN needs to be in conduit.
Is it your thinking that you could run THHN in walls without a raceway?
My BAD. I apologize. I did NOT see the NOT. I read but did NOT see!!!:mad: