590.4(G) interp.

Status
Not open for further replies.

Hendrix

Senior Member
Location
New England
Does this mean that a piece of ser run form a temp service, sleaved through a piece of 2" pvc, can be spliced just below the job trailer to another piece of ser and into the panel without a box ?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Does this mean that a piece of ser run form a temp service, sleaved through a piece of 2" pvc, can be spliced just below the job trailer to another piece of ser and into the panel without a box ?
Yes, that is what it means and no, it wasn't that stupid of a question.

Roger
 