Assuming the generator is big enough to supply the load is it ok to run 2 different transfer switches to feed two different services?
You dont bond the neutral in the genset its already done in the switchboards .
Assuming the generator is big enough to supply the load is it ok to run 2 different transfer switches to feed two different services?
Yes and no you can use a 3 pole transfer switch with a solid neutral if you like .
And have three different service feeds with the neutral bonded in each switchboard on one generator .
You dont bond the neutral in the genset its already done in the switchboards .