You might find Mr. Holt's calculator helpful..
http://www.mikeholt.com/documents/calculations/formulas/ResidentialLoadCalculations.xls
I think everyone around here uses 4/0 4/0 2/0 AL USE "sweetbriar." We don't usually use copper unless it's something other than residential.
I think everyone around here uses 4/0 4/0 2/0 AL USE "sweetbriar." We don't usually use copper unless it's something other than residential.
Hopefully not on the interior of the residence (if that's it's only rating)![]()
It will be run underground in conduit to the panel. I believe if it is "under" the house it is "not on the interior" of the house
But it is in the house where it terminates (assuming the panel is in the house) and if the only rating is USE, you can't have it in the house.It will be run underground in conduit to the panel. I believe if it is "under" the house it is "not on the interior" of the house
But it is in the house where it terminates (assuming the panel is in the house) and if the only rating is USE, you can't have it in the house.
I agree with Don, I missed or didn't pick up on the fact that you were intending on pulling USE in the conduit.
Roger