Here are two derating rules
"For operation at higher ambients, transformer
loading should be reduced 0.6% of rated KVA for each degree above
30?C average ambient to a maximum of 50?C (122?F). "
and from this thread,
"Load can be increased 1% per degree below 30 degrees C.
For every degree above 30 degrees C the load is decreased 1.5 %. "
I think it's possible to get the conductor to ambient thermal resistance or the conductor temp or some ratio relating these from just these numbers. Then using the 10 C insulation rule may allow pretty accurate lifetime predictions. This should also work for Romex lifetime predictions.
BTW, does anyone know the shelf life of transformers or of Romex?
Here are two derating rules
"For operation at higher ambients, transformer
loading should be reduced 0.6% of rated KVA for each degree above
30?C average ambient to a maximum of 50?C (122?F). "
and from this thread,
"Load can be increased 1% per degree below 30 degrees C.
For every degree above 30 degrees C the load is decreased 1.5 %. "
I think it's possible to get the conductor to ambient thermal resistance or the conductor temp or some ratio relating these from just these numbers. Then using the 10 C insulation rule may allow pretty accurate lifetime predictions. This should also work for Romex lifetime predictions.
BTW, does anyone know the shelf life of transformers or of Romex?