small 480 panel
Open Neutral
Inside the Beltway
Engineer
Have a case where an outbuilding ('the shed") will be ~800 ft from the main building, and needs routine generic power, i.e. say two 15 or 20A circuits. We have to run 480v to a building ("the barn") 300 ft of that distance, to run a VFD. I suggested we could extend the 480 the rest of the way to the shed, to reduce the conductors and voltage drop; and put a small stepdown in the shed.
The electrician says if we have more than that sole VFD 480 load, we'll need a 480V panelboard in the barn, and that's $800. I assume that's because most 480 panels are 3-phase, etc. Is there a less expensive solution for two single-phase 480v circuits; one for the VFD, the other for the line to the shed?
(This is in California, so the electrons must be politically correct....)
Each building must meet the requirements of Part II of Art 225.
I don't know of a reason that you could not tap off the 480v conductors outside of the barn and continue on to the shed.
How is the 480 terminating at the barn ? (Into a disconnect, etc).
In most cases the barn would have a distribution panel, etc for lighting, 120v supply, etc.