Romex stuff

Status
Not open for further replies.
Used to be you could use common sense in running romex through 2x4 studs and plates. (ex. 4-14/2 through a 1-1/4" hole.) Now, around here it is 2 wires, no exceptions. I know thats not set in stone and there are exceptions. What are they? TY
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I would say the "2" is a case of misunderstanding of the NEC.
The "rule" from 334.80 is:
Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).
 
Thanks Augie, now what constitutes "mantained spacing and in your opinion would, say 4-14-2 home runes in a inch and a quarter hole be permissable? how about 1 ko in a TJ?
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Thanks Augie, now what constitutes "mantained spacing and in your opinion would, say 4-14-2 home runes in a inch and a quarter hole be permissable?
You'll have to nailplate the stud faces with less than 1-1/4" of wood to the edge of the 1-1/4" hole. I never use more than a 3/4" bit in 2x4s.
 

tom baker

First Chief Moderator
Staff member
The local myth here is three cables. I have asked why and none one knows. It may be 3 is all you can get through a 3/4" hole. Or back when we had NM with 60 deg C insulation.
Even with 3 cables and NM-B thats not an issue as the derating is based on 90 deg c
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
In reality the code states you must derate when more then 2 cables are run thru a hole. However, since nm is rated 90C for derating purpose you can use 30 amps for #12 wire. 8 current carry conductor-- four 2 wire cables-- would derate 70%. 30 amps at 70% still leaves us with 21 amps. Thus we can be compliant with 4- 12/2 nm cables when bundled or thru a caulked hole.
 

iwire

Moderator
Staff member
Location
Massachusetts
However, since nm is rated 90C for derating purpose you can use 30 amps for #12 wire. 8 current carry conductor-- four 2 wire cables-- would derate 70%. 30 amps at 70% still leaves us with 21 amps. Thus we can be compliant with 4- 12/2 nm cables when bundled or thru a caulked hole.

I agree with Dennis. :)
 
As to when did it become an issue.............in the central coast and bay area it never was a few years back. It was common place to see a 2" hole in the upper plate (nail plated) and all the home runs comming through. I chose to do it a bit different and ran my subfeed in the middle and home runs to the outter holes. But I would often have 3 wires in a whole and no more than 2 at the subpanel connector. Same goes for the plate above a 4 or 5 gang box. Often times you would see 3 or 4 14's through a hole. No more. Thanks to all for the input. You fellas are great!
 

renosteinke

Senior Member
Location
NE Arkansas
When did it become an issue? The moment some 'home inspectors' bought code books and suddenly became experts. It was their agitating that led to the code being changed.

Ditto for the 'no Romex in damp locations' rule being extended so as to apply to virtually all crawl spaces. No matter that the IAEI has down-played the issue; any sign of moisture in the crawlspace, and you can't run your Romex down there.

Silly? You bet - but the sooner you realize that unqualified HI's, and other well-meaning folks, are hijacking the trade, the better our chances are of stopping them.
 

480sparky

Senior Member
Location
Iowegia
When did it become an issue? The moment some 'home inspectors' bought code books and suddenly became experts..........

HI's actually buy NECs? Thanks for the laugh..... I needed that. :roll:

NECs are way out of the price range for HIs. They're more likely to buy Code Check : Electrical.
 

renosteinke

Senior Member
Location
NE Arkansas
Yea, I appreciate the humor, too!

Still, it is in our own interest to monitor the various HI sites, just to see the 'unique perspective' of the posters. Heaven alone knows what code silliness they will next attempt.

Judging by what I have seen, HI forums are sorely lacking in folks with any real electrical knowledge.
 

jimport

Senior Member
Location
Outside Baltimore Maryland
Occupation
Master Electrician
Yea, I appreciate the humor, too!

Still, it is in our own interest to monitor the various HI sites, just to see the 'unique perspective' of the posters. Heaven alone knows what code silliness they will next attempt.

Judging by what I have seen, HI forums are sorely lacking in folks with any real electrical knowledge.

Ouch!
 

iwire

Moderator
Staff member
Location
Massachusetts
When did it become an issue? The moment some 'home inspectors' bought code books and suddenly became experts. It was their agitating that led to the code being changed.

Ditto for the 'no Romex in damp locations' rule being extended so as to apply to virtually all crawl spaces. No matter that the IAEI has down-played the issue; any sign of moisture in the crawlspace, and you can't run your Romex down there.

Silly? You bet - but the sooner you realize that unqualified HI's, and other well-meaning folks, are hijacking the trade, the better our chances are of stopping them.

Please show some real evidence of HIs changing the NEC.
 