I got the example problem working in a spreadsheet.  There were some typos in it which I fixed.
3 >enter number of conductors
0.09 > enter insulation thickness in inches
0.292 > enter conductor diameter [DC] in inches
0.576 > enter R-value of insulation on a per inch basis
3.2 >enter A' value
0.19 >enter B' value
2.15 >enter factor from table
0.95 >enter e value
1.315 >enter conduit OD
194 >enter Rdc at 75 C in uOhms
90 > enter TC, conductor temp in C
40 > enter TA, ambient temp in C
0.120 =calc'd I value in kiloamps
So, in principle, by using the OPs values I should be able to tell how hot the conduit should be. Or, given the conduit temp, the current flow necessary to get that temp.
3.2 >enter A' value
0.95 >enter e value