I have been looking for a code reference for a local rule here in Peoria IL.
The inspectors here require an Service Disconnect if the panel will be more than 5 feet away from the meter.
I can not find anything that specifically requires an additional disconnect means within 5 feet from the meter.
The only code that I can find with any reference to location of Disconnect means is 230.70(A)
I would like to know if there is a specified distance in the code or if it is just the AHJ setting 5 foot as the "nearest the point of entrance of service conductors".
Thanks
The inspectors here require an Service Disconnect if the panel will be more than 5 feet away from the meter.
I can not find anything that specifically requires an additional disconnect means within 5 feet from the meter.
The only code that I can find with any reference to location of Disconnect means is 230.70(A)
(A) Location. The service disconnecting means shall be installed
in accordance with 230.70(A)(1), (A)(2), and (A)(3).
(1) Readily Accessible Location. The service disconnecting
means shall be installed at a readily accessible location
either outside of a building or structure or inside nearest the
point of entrance of the service conductors.
(2) Bathrooms. Service disconnecting means shall not be
installed in bathrooms.
(3) Remote Control. Where a remote control device(s) is
used to actuate the service disconnecting means, the service
disconnecting means shall be located in accordance with
230.70(A)(1).
I would like to know if there is a specified distance in the code or if it is just the AHJ setting 5 foot as the "nearest the point of entrance of service conductors".
Thanks