I need to order about 2000m of cable for a few different runs. Just want to make sure im right.
One length is 290m, at 120v, and need to maintain a constant 11A. would anyone be able to assure me that I need a #4awg? Thank you
 
I need to order about 2000m of cable for a few different runs. Just want to make sure im right.
One length is 290m, at 120v, and need to maintain a constant 11A. would anyone be able to assure me that I need a #4awg? Thank you

sorry I will explain a little better. I need to mailtain 11A at the load, a rectifier. will the calculation I came up with a 3c/#4 be correct? seems really big.
 
It makes a difference if you share the neutral.

If you have (2) 11 amp, 120V circuits with continuous loads, and you share the neutral, its like having a single 240V circuit (or 208V circuit if you have a three phase source).

So the % voltage drop could be half.
 
Thank you for your replys. not sharing neutral but might have to and I did that calculation at 5% vd. I have a problem with number #1awg because I can only fit a #4 into a 15A breaker with out using barrel lugs then into the breaker and changing lugs at the rectifiers. Thanks
 
One length is 290m, at 120v, and need to maintain a constant 11A.
That's about 950 feet. I'd look into boosting the voltage (or at least start with a higher voltage) and stepping it down to 120v at the load end.
 