Brandon Loyd
Is it legal to trim strands from a wire that is oversized for voltage drop, to fit into the smaller lugs of a breaker?
			Nope. How would you comply with 310.11(A)(4)? What is the trimmed wire size?
How about 110.3(B)?
I can hear the manufacturer saying "Sure, give it a haircut..."
Splitting hairs on that reference article? I do not think it applies.
OP......While I am fairly certain it is a violation, I am not sure what article makes it a violation. The one above clearly (IMO) is not the right one.
I just connect a smaller conductor to the larger conductor to connect/fit the device.
Okay, if I cut two strands off a 4/0 conductor, what is my wire size and circular mil area. Ampacity is ?. The original marking no longer applies IMO.
(4) The AWG size or circular mil area.
According to table 8, Chapt. 9 of NEC 08, a 4/0 conductor has 19 strands whose diameters are .106 in. If you cut two strands, the area of the conducting material would be reduced from 0.168 sq. in to 0.150 sq in., about an 11% reduction.
I do not think the ampacity of a conductor can be calculated that way.
Note that I did not mention ampacity.
Only for the half inch or so at the end. You'd still have full cross section for the rest of the cable length.about an 11% reduction.
These crimp-ons greatly reduce the cross section: half the dia. gives you 1/4th the cross section which is 4x the resistance per unit length. Once crimped this ratio will be slightly smaller.
I'd think then the rule is only for mechanical reasons.
The crimps have the one thing we need,U L listed