Art. 310 Ambient temp tables 2011
wireguy8169
Southern Maine
When would you use Table 310.15(B)(2)(a) versus Table 310.15(B)(2)(b). This came up in class this evening and for the life of me could not find an answer, they did not even cover that in my code change class.
Thanks
Yeah that what I said, I noticed it when planning for my class, but could not find any explaination anywhere in either of my code update books, I felt bad cause I did not have an answer and I am not afraid to say I do not know. I knew it was going to be one of the first questions I was asked. So my mission is to find an answer...
thanks
It tells you which one to use depending on which ampacity table you are using.
All they did was consolidate the various ones that were at the bottom of each table and add a few more temperatures.
Thanks for the responses,
Jumper is what your saying is if your using Table 310.15(B)(16) you would use table 310(15)(B)(2)(a)
of using Table 310.15(B)(17) you would use 310.15(B)(2)(b)?
You posting that and reading it a few more times, seems logical. then if you have more than three current carring conductors you would have to further derate as before using table 310.(15)(B)(3)(a).
Thanks
Thanks
Close-- Jumper got it- I didn't realize that 310.15(B)(18) was based on 40C. So it is T. 310.15(B)(18) that would use T. 310.15(B)(2)(b) or any other table that is based on 40C. Tables 310.15(B)(18-21)