Overcurrent Protection for MV Feeders

Status
Not open for further replies.

ron

Senior Member
240.4 clearly indicates that conductors need to be protected against overcurrent in accordance with their ampacities ....
It specifically refers to 310.15 which is 0-2000V.
Where is the requirement for overcurrent and/or short circuit protection for conductors >2000?
240.4 doesn't specifically exclude conductors >2000V, but the reference to 310.15 leaves me with nothing to go by.

I have a 15kV feeder that I will protect with 50/51 protection (overcurrent and short circuit protection), but I'm trying to figure out for this vveerryy long radial campus feeder whether there is any way I can reduce the ampacity of the feeder as I go along from building to building and the calculated load is less and less.

Thanks
 

dkidd

Senior Member
Location
here
Occupation
PE
I'm trying to figure out for this vveerryy long radial campus feeder whether there is any way I can reduce the ampacity of the feeder as I go along from building to building and the calculated load is less and less.

Thanks

Have you considered fused sectionalizing switches?
 