overhead clearance(230.24 (B)(2)

Status
Not open for further replies.

nizak

Senior Member
Point of attachment of weatherhead on the house is 12'5". As long as I maintain that height,am I responsible for what the Height of the POCO's service drop ends up crossing the driveway at?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I think you are responsible to establish a point of attachment that will keep their lines up to a specified height. We are not responsible for the poco lines per NEC however they may refuse to hook it up if your attachment point doesn't give them the clearance they require.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
When that happens here, the question becomes "who is going to pay for the pole added to maintain the correct height".
 

tmason

Member
i would ask a couple questions how far is the span and what type of structure is it a mast service may be needed to keep the clearence
 