Looking for some opinions on the following scenario.
I sometimes have to troubleshoot controls on older equipment where the control voltage is >50V, typically 120VAC on 480V powered units. Our location's live work policy meets 70E, no live work unless it's approved by the plant manager and you filed the appropriate paperwork and he usually says "no".
The troubleshooting iteration typically is to power off, LOTO, add probes to likely points to locate the problem, close the door, re-energize and see if you guessed correctly where to place the probe points.
Per the standard:
NFPA 70E Article 130.1 Justification for work. Live parts to which an employee might be exposed shall be put into an electrically safe work condition before an employee works on or near them, unless the employer can demonstrate that deenergizing introduces additional or increased hazards or is infeasible due to equipment design or operational limitations.
What if:
1) The main power remains under LOTO so there is no chance for Shock, Flash, or Boom.
2) The control power supply is disconnected from the stepdown transformer where it normally supplies the 120VAC. (No backfeeding to the primary of the transformer.)
3) A separate source of 120VAC is used and run through a GFCI outlet or breaker and is then used to power the 120VAC control circuit.
Since a GFCI by its nature limits current flow to around 5mA within 25 ms prior to tripping, wouldn't this "put into an electrically safe work condition" the equipment so that the control functionality could be tested live?
Additionally, do you think a "Live Work Request" needs to be filed each time this is done?
I sometimes have to troubleshoot controls on older equipment where the control voltage is >50V, typically 120VAC on 480V powered units. Our location's live work policy meets 70E, no live work unless it's approved by the plant manager and you filed the appropriate paperwork and he usually says "no".
The troubleshooting iteration typically is to power off, LOTO, add probes to likely points to locate the problem, close the door, re-energize and see if you guessed correctly where to place the probe points.
Per the standard:
NFPA 70E Article 130.1 Justification for work. Live parts to which an employee might be exposed shall be put into an electrically safe work condition before an employee works on or near them, unless the employer can demonstrate that deenergizing introduces additional or increased hazards or is infeasible due to equipment design or operational limitations.
What if:
1) The main power remains under LOTO so there is no chance for Shock, Flash, or Boom.
2) The control power supply is disconnected from the stepdown transformer where it normally supplies the 120VAC. (No backfeeding to the primary of the transformer.)
3) A separate source of 120VAC is used and run through a GFCI outlet or breaker and is then used to power the 120VAC control circuit.
Since a GFCI by its nature limits current flow to around 5mA within 25 ms prior to tripping, wouldn't this "put into an electrically safe work condition" the equipment so that the control functionality could be tested live?
Additionally, do you think a "Live Work Request" needs to be filed each time this is done?