CH Breakers HACR

Status
Not open for further replies.

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
HACR testing has been a standard part of UL489 for maybe the past 15 years or so.
Since this time, breakers are no longer required, by UL, to carry HACR labels.

Several manufacturers offer 'HACR' labeled breakers, at a price, for those few AHJ's that require one.
 

stevebea

Senior Member
Location
Southeastern PA
HACR testing has been a standard part of UL489 for maybe the past 15 years or so.
Since this time, breakers are no longer required, by UL, to carry HACR labels.

Several manufacturers offer 'HACR' labeled breakers, at a price, for those few AHJ's that require one.

Thus my question. I have an inspector that insists on seeing the HACR label. :roll:
 