I am not sure where you think there are paralleled conductors here. Maybe I am missing something obvious in the photo.
The neutral bar in the photo can't be bonded to the EGC as shown. I'll be removing the bond. Removing that EGC/Grounded Conductor bond contains the neutral current on the insulated white conductors, which are all in the same raceway. From the old panel JBox to the Service center, all the conductors of multiple circuits are in a single common raceway.One could also argue that by connecting two neutrals from a different circuit that the conductors of the same circuit are not contained in the same raceway, etc. 300.3(B). When you parallel the neutral current will take all paths, as you well know.
So you're saying your opinion is that the Parallel Conductor Rule prohibits paralleling conductors smaller than 1/0?BTW, I disagree with the argument about paralleling that you referenced. In fact, I think someone made a proposal to change it and it got rejected because the cmp thought it was clear-- I think....
Also wouldn't the neutrals need to be paired with their respective ungrounded conductor?
Thanks for the clarification, Dennis.Is it a big deal to just use wirenuts? Also wouldn't the neutrals need to be paired with their respective ungrounded conductor?
That eliminates the parallel issue, but I still think the best fix is to form as many 3-wire MWBC's as you can using those new white wires. I count five, which gives you neutrals for 10 circuits.How are there any paralleled conductors here?
200.4 Neutral Conductors. Neutral conductors shall not be used for more than one branch circuit, for more than one multiwire branch circuit, or for more than one set of ungrounded feeder conductors unless specifically permitted elsewhere in this Code.
That install will not be legal in 2011.
Article 200.4 Neutral Conductors
isn't the new neutral in the same raceway as the hots that it is associated with?