Isn't 110.14 C in direct conflict with 110.14 (1) (a)2 and 3
In other words let's say I'm using #12 THHN 90 degree wire (dry location) 6 curent carrying conductors in a 3/4" raceway.The way I read 110.14 c is that I can use the 90 degree column 310.16 for ampacity adjustment, which after derating per 310.15 b 2 a The ampacity of the wire would be 24amp
However when I read on 110.14 (1) (a)2 and 3 This tell me either use 60 degree column or 75 degree if the termination is rated as such. Now doing the same calculation above but using 75 degree column I'm at 20amp.
What am I missing one says I can use 90 degree column and the other tells me i can not.