Two machines and a lighting load are connected in parallel to a 220 V, 60 Hz line. The first machine uses 40 kW of power at 0.81 power factor lagging. The second machine uses 27 kVA at 0.93 power factor leading. The lighting load consumes 13 kW. What is the current in the line feeding the three loads? What kVAR value of capacitance connected across the line is necessary to obtain a power factor of 0.98 lagging? With this capacitor installed, what will be the current flowing in the line feeding the four loads?
Could any one help me with this one?
Thanks!!
In any problem, first thing is to decipher what you are looking for. In this case the system current, NOT each load current.
Second thing to do is state your assumptions, i.e. 220V is line-line/single-phase, the lighting load is operating at 1.0 pf, and the loads always operate simultaneously.
Next, calculate your system current adding up the load KVA values, then divide by the voltage. Not so straight forward in your problem because you do have a leading pf for one load, so, lagging and leading come into play.
Determine the KVAR from each KVA. This is where it gets tricky because you need to understand the power triangle/trigonometry/complex numbers/vectors.
KVA = P + jQ where KVA is a vector
and,
KVAR = KVA * (sin(acos(pf)) (lagging)
KVAR = KVA * (sin(-acos(pf)) (leading)
To determine the "system" pf and current:
KVA = (40+25+13)KW + j(29-10-0)KVAR
KVA = 78KW + 19KVAR
|KVA| = sqrt(78KW^2 + 19KVAR^2)
|KVA| = 80.3KVA ( This is the magnitude)
I = 80.3KVA/220V
I = 365A (confirms
david luchini post)
The system pf is therefore;
pf = KW/KVA
pf = 0.97
In the next step you need to improve your PF by going from 0.97 to 0.98
Take desired system pf and determine system KVAR, then subtract old KVAR from new KVAR. Another way to look at it is the amount of capacitance (-KVAR) that you need to add, noticing that the KVAR "added" is a negative (capacitance) value.
KVAR added = KVAR(new) - KVAR(old) = 16KVAR - 19KVAR = -3KVAR or 3KVAR of capacitance
Little play on words in the problem to trip up the unwary in saying determine the current in the four loads, as they are meaning the capacitor as the "fourth" load.
KVA = (40+25+13+0)KW + j(29-10-0-3)KVAR
KVA =78KW + 16KVAR
|KVA| = 79.6KVA
Current is calculated the same as earlier;
I = 79.6KVA/220V
I = 362A (confirms
david luchini post)
That is a lot of cost to go from what would already be considered a very good PF, to a new very good PF, and only reduce amps by 3. But hey, nobody ever said book problems are practical..........