Is the "California 3-way" switch wiring permissible according to the NEC?

Let me define a "California 3-way" for the sake of this post. I am defining the California 3-way as : a wiring of 3-way switches where the common terminals and one hot terminal of the switches are used as the travelers for the circuit. The other hot terminal of each switch is connected to the same phase wire that provides voltage to the circuit. The load for the circuit makes connection the traveler that connects the hot terminals together.

With that definition, is a California 3-way permissible according to the NEC?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Is this what you have? If so it may be complaint with nm cable but not with metal raceways.

300px-3-way_switches_position_2.svg.png



Depending on where the neutrals are wired you may have parallel neutrals.
 
Last edited:

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
Is this what you have? If so it may be complaint with nm cable but not with metal raceways

300px-3-way_switches_position_2.svg.png

no, that is not what I am describing. What I am describing is the use of two 3-way switches in a circuit used to control a light while the rest of the circuit continues downstream to feed an additional load.
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Since all the switching is done in the ungrounded conductor, what code would cause this to be non compliant?

If the neutral were fed thru and tied together on both ends from different place then you would have a parallel path.. 310.4
 

realolman

Senior Member
Is this what you have? If so it may be complaint with nm cable but not with metal raceways.

300px-3-way_switches_position_2.svg.png



Depending on where the neutrals are wired you may have parallel neutrals.

I must be missing something ... this looks pretty normal to me.... Man, I hope to never come across that other stuff
 
Last edited:

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
this is what I am describing Denis.
If you turn off the left hand switch in the post-it sketch, the hot is running on both a traveller and the common to common conductor, which is the parallel condition. 310.4 prohibits conductors smaller than 1/0 from being in parallel.

It was a neat little switching setup in its day.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If you turn off the left hand switch in the post-it sketch, the hot is running on both a traveller and the common to common conductor, which is the parallel condition. 310.4 prohibits conductors smaller than 1/0 from being in parallel.

It was a neat little switching setup in its day.

I agree with AL. This is definitely parallel neutrals
 

hurk27

Senior Member
Here's what I was always told was a travling buss three way/ tunnel switch?
Flip the first switch and first light comes on, flip the second switch and first light goes out and second light comes on and so on, flip the last switch and last light goes out.
Traveling3-ways.jpg
 
Last edited:

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Here's what I was always told was a traveling buss three way/ tunnel switch?
Wayne, it makes sense that the tunnel switching setup would have the moniker "traveling bus", as both the hot and neutral are on the travelers.

I had never heard the term "traveling bus" until an old Forum member, Benny, used the term for this sketch of mine:

img33.jpg


This shows an expanded "California Threeway" between two buildings, incorporating 4way and 3way switches, the ability to control lighting in common at both buildings, and to supply receptacle outlets at the far building.

However, the "bus" is a hot on one traveler running between the pair of 4ways, only.

Wayne, I think your application more accurately deserves the title "traveling bus".
 

jap

Senior Member
Occupation
Electrician
If you turn off the left hand switch in the post-it sketch, the hot is running on both a traveller and the common to common conductor, which is the parallel condition. 310.4 prohibits conductors smaller than 1/0 from being in parallel.

It was a neat little switching setup in its day.

I agree that this creates a parallel condition in "that particular part of the circuit", but, what harm does that cause? It's not like where you use 2 smaller parallel conductors from the beginning,to add up to the amperage of a larger conductor. To me, "Both Ends" would mean starting at the breaker with parallel conductors to the first termination point,like you would if you were parralleling (2) smaller conductors to take the place of a larger conductor on a large feeder.On this circuit it starts out as a single conductor then gets paralelled in the middle.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
To me, "Both Ends" would mean starting at the breaker with parallel conductors to the first termination point,like you would if you were parralleling (2) smaller conductors to take the place of a larger conductor on a large feeder.On this circuit it starts out as a single conductor then gets paralelled in the middle.

Submit a proposal to change the wording of 310.4 to allow conductors to be installed in parallel if each conductor is rated according to the OCPD. Until the code definition is changed, then it is as Al and Dennis say: an extremely small misinstalled parallel conductor.

Bear in mind, 300.3(B) already puts some constraints on this principle.
 

480sparky

Senior Member
Location
Iowegia
Submit a proposal to change the wording of 310.4 to allow conductors to be installed in parallel if each conductor is rated according to the OCPD. Until the code definition is changed, then it is as Al and Dennis say: an extremely small misinstalled parallel conductor............

The language already exists. It just doesn't allow it for supplying receptacles and luminaires.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree that this creates a parallel condition in "that particular part of the circuit", but, what harm does that cause?

Well it probably does cause harm directly but it will create unnecessary electro magnetic fields. I for one would prefer not to have them in my house however the NEC is silent on that issue.
 