Using 60 degree ampacity for less than 100A

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
what is that rule this is a single fam dwelling with a 200 amp service i put a 100 amp brk in the main panel and put a main lug with a 90 amp brk and a retention clip in the garage that is detached so would you say that would safice for the rule
That would work but remember if you are under the 2008 NEC you would need 4 wires and you also need to use ground rods or other electrodes.
 

tmason

Member
yes to be exact i ran four no 4 thhns to the garage installed the panel two ground rods and bonding bridge
 