iwire:
Clearly a series circuit has great advantage in an airport type application for wiring over long distances with individual loads that are low voltage, 10 to 120 V would be low voltage. Also the lower the lamp voltage the more rugged is the filament.
Under on-off conditions lamp life should be increased because of the reduced filament stress on turn on with a constant current source.
However, a big disadvantage of a series string of lights is that if one burns out, then all in that string go out. Very little was said in the article on this subject. However, that does not happen in the airport application according to the article, but no explanation of how this is accomplished. Quite obviously this means the individual fixtures have built in sensors that detect lamp burn out and then short across the failed lamp when such failure occurs.
broadgage:
There are very few "real world" constant current loads that might be connected to a utility or similar supply.
The series street light lighting example given above is not much used these days, but anyway, it does NOT draw a constant current from the utility. It supplies a constant current to the lamps, regardless of changes in lamp volts or utility voltage. This means that the current drawn from the utility mains is variable.
If you use something like a Variac to maintain a constant current to a lamp load, then it is also a constant voltage source to the lamp under constant lamp conditions, and also a constant load power on the system. Thus, as the mains input voltage goes up the mains current goes down.
On the other hand if a large source voltage is used and an appropriate series inductor is used for current limiting, then the mains see an an approximately constant current load.
Fluorescent lamp ballasts "try" to supply a constant current to the lamps, but the supply current from the utility will vary according to line voltage and lamp type.
Following are measurements on two magnetic ballast fluorescent fixtures.
One 8' fixture
140 V 0.92 A 129 W
130 V 0.92 A 124 W
120 V 0.95 A 119 W
110 V 1.02 A 114 W
100 V 1.09 A 111 W
The current is considerably more constant than the voltage and thus approximates a constant current load.
Different 8' fixture
140 V 0.95 A 112 W
130 V 0.86 A 104 W
120 V 0.83 A 99 W
110 V 0.89 A 96 W
100 V 0.92 A 92 W
Again relatively constant.
A cheap electronic ballast unit, 4' instead of 8'.
140 V 0.83 A 79 W
130 V 0.81 A 73 W
120 V 0.72 A 66 W
110 V 0.62 A 58 W
100 V fails to light one bulb
A good electronic ballast should be able to provide constant light output, constant current thru the bulbs, and be a constant power load on the mains.
.