qcroanoke
Sometimes I don't know if I'm the boxer or the bag
- Roanoke, VA.
- Sorta retired........
take 1 #6 and series through the ground rods or do I need to run a #6 to each rod?
And make sure that they are between 6' and 12' apart.Yes you can. It is done all the time, and code compliant.
Why 12'?
Yes.......... What's so special about 12'?
I don't know. Must be the Flexril for the pinched nerve in my neck.Yes.......... What's so special about 12'?
You're using 6' rods??![]()
I figure the zone of influence is the length of rods installed. 8' rods get 8'of separation. 10' get 10'.
I should have said "make sure they are at least 6' apart".:roll:I don't know. Must be the Flexril for the pinched nerve in my neck.
6' rods would be a violation. 250.52(A)(5).
Notice the
What is the 'zone of influence'?
Paralleling efficency of ground rods is best when they are twice the length apart or 16 ft for 8 ft rods. When driven electrodes are closer than 6ft together, the concentric shells of the earth overlap, and the two rods function as one.
Has anyone ever shown there is any special benefit in general from having a lower earth resistance?
Thus, two-rod installations are common, but are they necessarily correct?