Question: Does 1910.305(g)(1)(iii) suggest that flexible wiring and cables cannot be run through walls, ceilings, floors, doorways, windows, or similar openings when used in temporary service applications? Or, does this section only prohibit the practice when used as a substitute wiring method in permanent applications?
Response: In accordance with 1910.305(g)(1)(iii), flexible cords may not be used in permanent installations as specified in (A) through (E) below:
(A) As a substitute for the fixed wiring of a structure;
(B) Where run through holes in walls, ceilings, or floors;
(C) Where run through doorways, windows, or similar openings;
(D) Where attached to building surfaces; or
(E) Where concealed behind building walls, ceilings, or floors.
When these cords (including extension cords) are used in temporary wiring installations, 1910.305(a)(2)(iii)(G), allows them to run through doorways or other pinch points, such as windows or other similar openings, provided they are protected from damage. This provision does not, however, except them from the other four prohibitions, (A), (B), (D), and (E) above.
In other words, flexible cords when used in temporary wiring may be run through doorways, windows, or similar openings provided they are protected from damage, but cannot be used as a substitute for the fixed wiring of a structure; run through holes in walls, ceilings, or floors; attached to building surfaces; or concealed behind building walls, ceilings, or floors.