natfuelbill
Why does the Code require GFCI receptacles in garages and hangers, but not on process, industrial and manufacturing floors?
Downtime in these places due to nuisance tripping is bad for business? Yet car washes now require them even though there has never been an 'incident.'. . .but not on process, industrial and manufacturing floors?
I wish Section 590.6 weren’t quite so convoluted. What is now (or has become) Section 590.6 has been chopped up and “wordsmithed” so much it isn’t immediately clear. However, read carefully and parsed correctly, Section 590.6, in combination with Subsections 590.6(A) and (B), essentially requires GFCI or an Assured Equipment Grounding Conductor Program (AEGCP) in virtually every “workplace” operation.Why does the Code require GFCI receptacles in garages and hangers, but not on process, industrial and manufacturing floors?
The oldest version I have readily available is 1993; it said:I wonder when this GFCI was first placed in this section, or past section that have been renumbered to 590.6.
It's older than that.305-6. Ground-Fault Protection for Personnel. Ground-fault protection for personnel on construction sites shall be provided to comply with (a) or (b) below.
(a) Ground-Fault Circuit-Interrupters. All 125-volt, single-phase, 15- and 20-ampere receptacle outlets that are not a part of the permanent wiring of the building or structure and that are in use by personnel shall have ground-fault circuit-interrupter protection for personnel. If a receptacle or receptacles are installed as part of the permanent wiring of the building or structure and used for temporary electric power, GFCI protection for personnel shall be provided.
Don't kid yourself. Have you ever tried to make a Proposal?... otherwise it would disappear overnight.
No, but I have to wonder if there is an awful lot of unexplained inertia in adapting new and good ideas. Is it just bureaucracy and egos?Don't kid yourself. Have you ever tried to make a Proposal?
Assuming the "industrial exception" doesn't apply, while GFCI does not have to be part of the receptacle, it still must be provided.
Article 590 applies to temporary installations only. See 590.1 Scope. Permanent receptacles in any environment are out of scope for 590.
QUOTE]
For 2011 NEC - how do you read 590.6(A)(2)?
Temporary permament receptacle....cOnFlIcTeD ????
Or am I missing something obvious?
This 590.6(A)(2) section seems to be more OSHA than NEC.
QUOTE]
You are missing something counter-intuitive due to language limitations.
Permanent as in used for portable equipment that is a part normal operations. Sweepers, fans, laptops, etc. No GFCI.
vs.
Temporary as in used for (590.3) construction et al. Floodlamps while replacing overhead luminaires. GFCI needed.
I understand what you wrote, but, how is a sweeper, fan, laptop etc not considered maintenance as used in 590.6(A)?
Maybe some more examples of tasks that are not maintenance...and therfore not requiring GFCI.
This seems like such a fine distinction.
Here is the Websters Dictionary definition for maintenance.
"the upkeep of property or equipment"
Here is the Websters Dictionary definition for upkeep.
"the act of maintaining in good condition : the state of being maintained in good condition"
You need to stop focusing exclusively on the text of 590.6 and remember 590.6 is used only if 590 applies.
590.1 gives the scope and 590.3 gives examples. Unfortunately the word maintenance in 590.3 is a multi-use, personally interpreted word for most people. Thereby a source of understandable confusion. Look at the other examples and notice their scope of content. All are "major" items, quotes emphasized.
So if you're going to bring in a floor scrubber every night - it's housekeeping not maintenance. If you're going to shut down for the day to power wash - it's maintenance not housekeeping.
A fan to ventilate dangerous fumes during a toxic cleanup is temporary while a fan to cool off workers on a production line is just portable equipment using a receptacle.
Most of the words that tie this article down are judgemental. Everybody is going to draw a line at a different place. Just remember that the article is not meant to interfere with day-to-day operations but only to apply to exceptional jobs. So if a millwright comes out to lag a machine down to the floor it's not day-to-day even though it takes only 15 minutes. That hammer drill requires GFCI. IMHO.
I agree; however, there is no intermediate term between permanent and temporary - and no provision in Article 590 to do anything else even if there were.... remember 590.6 is used only if 590 applies.
Where in the Article's scope does it say that?... Just remember that the article is not meant to interfere with day-to-day operations but only to apply to exceptional jobs... IMHO.