For the past 2 days, I've been constantly getting a ground fault alarm (we have an ungrounded system here) on one of our 480V MCC bus. The alarm toggles simutaneously with the run status of a pump we have. (we have a DCS system here that we can monitor). So, it's simple, we isolate the pump, and check service/load.
We got electricians check it, each phase-to-gnd megged good (2 Gohms), he disconnected the leads from the load side of the starter, and pulled the starter close, and no ground alarm; then he re-connected the leads back to the load side of the starter, and ran the motor, again, no ground alarm either, and from this point on, we no longer get this ground fault as we run the motor.
Just some background info
The pump is on a level control, so it's not continous run
Motor FLA=86amp, 3-PH, 75HP, SF=1.15, 480V
it was measured that the motor was pulling approx. 100amps when it run
could it be possible that something (thermally) is going on inside the motor? as I know the motor is overloaded at the moment, which is a seperate issue we've been working on, but could it be this causing some intermittent insulation problem which then causes a ground fault alarm?
At the time writing this, the motor kicks on/off with a level control, and no ground alarm is observed at the moment. kinda mysterious here.
Any input is welcome. Thanks.