Neutral Bar Needed??

Status
Not open for further replies.

360Youth

Senior Member
Location
Newport, NC
A friend called me up to pick my brain about an install. Not sure I was much help, go figure. Here is what he had:

CT Cabinet-Fused Service Disconnect-ATS-MDP, 3-phase

The service disconnect came with no neutral bar. Can he run his neutral from the CT cabinet straight through the service disconnect to the ATS, and bond the disconnect from the CT and the ATS from the disconnect? Neutrals and grounds separated at the ATS as normal. I will have to look it up when I get home, but wanted to have some input from the members as well. Thanks. Hope I explained it sufficiently. Let me know if I did not.

Thom
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Augie definitely found you one.

I was going to say what I usually see on the inside of potential service disconnects is a sticker that says "suitable for use as a service disconnect if neutral/bond kit xxxx is installed."
 
Status
Not open for further replies.
Top