What criteria are used when sizing a generic 3 phase, 480V welding receptacle in an industrial plant? xxx
The question has arisen from a need for temporary power for a turnaround. The owner wants to connect to a welding receptacle to feed a 480/120V transformer to feed a tool/equipment trailer (amperage requirements appear to be within reason based on breaker size). xxx
xxx I guess what I'm trying to get at is regardless of this specific need, if I were to sit down and specify a welding receptacle's conductors and OCP without knowing the exact equipment, what would I do?
After the plant is built, "Welding Receptacles" in industrial plants are used 1000:1 for temporary power over actually powering a welding machine. Your example of the equipment trailer temporary power is a normal use.
So, how to specify a "welding receptacle" feeder - when you don't know what you are going to feed?
First, regardless of the name - "Welding Receptacle" - these are general purpose receptacles. Art 630 is not much of a concern.
I would start with doing some homework. You have to get familiar with the clients needs. Since they can't tell you, you have to figure it out - that's part of the engineering. And, yes, you are doing engineering.
1. Go look at existing WR feeders - wire size and OCP. Get the nameplate data from the existing receptacles. Hopefully there will be some uniformity.
2. Go to the maintenance department and see what they have for welding machines. Get the nameplate data. Go to the plant construction manager. Ask what the contractors bring in for welding machines. You may have to call your favorite contactor and ask what they have.
3. Also ask (both maintenance and construction) what other equipment is regularly plugged into these receptacles. Get the nameplate data.
How far you go is up to you - just remember, you are the engineer of record.
Compare the existing spec with the intended use. They should match - after all, the receptacles are being used. If so, make your new one match (as long as it meets code for wire size, OCP, receptacle).
If the existing spec doesn't match - the intended use is more power than the existing receptacles can supply - the people you are asking aren't telling the truth. They are likely telling you what they would like to see. I don't have any suggestions to fix this.
After all this is done and you feel comfortable with the clients needs (as opposed to wants), my experience is that 99.99% of all the WRs I have seen, or specified and installed, have been 60A OCP, 60A conductors, 60A 4W receptacles - no neutral, no 277V loads. Any equipment requiring more power gets a temporary (art 590) direct connection to an MCC bucket.
Good luck. Let us know how it coes out
So sayeth the worm