Nope, I was just making the point that one electrode was needed what ever the case may be, you are trying to read to deeply into my words.
That could be. I'll give it my all to stop
Not that I see
Here I think you are saying the issues of 250.190 are not a concern. (Or maybe I'm reading too deep (;-)
If so, I disagree. I'm not looking at code minimums, I'm looking at good design. I think it is important to have the relaying operate prior to the shields turn into vapor. And I think the issues of art 250.190 are an important part of that. Even the utilities are concerned with that aspect.
And how do you know this is not a utility or privately owned transformer under NESC rules?
I don't. But the OP doesn't feel like a utility. And his (or possibly "her") occupation is listed as "building engineer". I think likely not - but then again --- i don't think it matters much
I work at Universities in NC that are their own POCO's and I must admitt this is partly included in my comments.
I truly feel your pain. Twenty five years ago, I spent a bit of time as a university power plant - plant engineer. The EE department PHDs occasionally came up with bad dream designs that could only be built out of unobtanium - yuck
I guess you missed the part where the OP was grounding the sheilds to an electrode that was jumpered to the secondary electrode.
No, I did not miss that part. Considering my current understanding of medium voltage power system feeders, I think that tying the primary power feeder conductor shields to a ground rod (which includes the secondary neutral and likely the xfm case) and not considring the relaying aspects, to be poor design pratice. It wouldn't matter if it was utility or private.