I don't typically get into generator fuel tank sizing but I did on this particular project. Does anyone have any good references on how much fuel (diesel) a generator uses. Preferebly a table showing KW values and the respective fuel consumption per hour or per day.
I have a reference that says a 225 KW generator (diesel) uses 16.6 Gallons per hour. I need the generator to run for a week continuously at full load.
(16.6)(24)(7) = 2789 gallons total including the day tank.
Im only using this for preliminary design purposes. Someone from another company said it would require about 3 times that amount or upwards of 10,000 gallons.
Obviously this will be properly designed with manuf. actual specs but I need to have a preliminary.
Thanks for the help
Thanks for the help