Hi guys, wondering anyone can help clarify a disagreement on a fire pump installation where we both interpret the code a little differently.
Referring to NFPA 20 Chapter 9
We are installing a fire pump in a 3 story building.
There is no backup generator and none is required as they have been deemed to have reliable power and the building size is within the local fire dept. pumping capacities.
The normal source of power though.... We interpret that we would need to pull off power before the main disconnect to the building (and metering cabinet).
Our client interprets the code a little differently, believing that they can pull power from a circuit directly off a power panel (which has a couple disconnects in line before it, ie. main disconnect switch and a disconnect switch for the panel).
Thanks in advance to anyone who can clarify.
Mike V, EIT
Referring to NFPA 20 Chapter 9
We are installing a fire pump in a 3 story building.
There is no backup generator and none is required as they have been deemed to have reliable power and the building size is within the local fire dept. pumping capacities.
The normal source of power though.... We interpret that we would need to pull off power before the main disconnect to the building (and metering cabinet).
Our client interprets the code a little differently, believing that they can pull power from a circuit directly off a power panel (which has a couple disconnects in line before it, ie. main disconnect switch and a disconnect switch for the panel).
Thanks in advance to anyone who can clarify.
Mike V, EIT