bilwei
- Lufkin, Texas
Intro Info; The owner of a new building has hired me as a 3rd party to look into the electrical system after the owner encountered burned wiring resulting in numerous electrical issues. I will only ask an opinion on one of these issues at this time. I have a building with 2 X 4 lay in troffer fixtures thru out. The electrical contractor that wired the building has installed MC cable (switch leg only)from fixture to fixture and made joints in each fixture. The AHJ has issued a final green tag & Certificate of Occupancy. I asked the AHJ about this particluar installation and refered him to Section 410.31. AHJ response; contractor did not use the fixtures as a raceway. Since there is only a joint made up in the fixture and they are are only dealing with a switch leg and not feeding a branch circuit thru to other electrical apparatus therefore it is not a code violation. What say yee