Bob,
A fan, a floor sweeper, or a laptop are "appliances" or other "utilization equipment" not temporary electric power as required by the scope 590.1; Therefore the article is applied to the receptacle not the appliance.
A permanent receptacle is placed for the use of appliances and other utilization equipment. The use of that equipment is inherently temporary but the electric power is permanent.
The article addresses wiring for temporary electric power, not temporary work.
The confusion arrives in 590.6(A) where a clause was added to close a loophole. Roughly equivalent: If you are doing work that would normally require the installation of "temporary electric power" then you cannot bypass the GFCI requirement by borrowing "permanent electric power".
As to its intent not to interfere with day-to-day operations, that's where the IMHO In My Humble Opinion comes into play. Thought that acronym was common enough. Guess not.