Does all grounded switch gear over 1k amps automaticly come with gfci protection?
My bad, meant GFP.See section 230.95 of the NEC. (Ground-Fault Protection of Equipment. NOT GFCI)
I agree with 230.95. I have a problem with a GFP 1600amp 277/480v service that keeps tripping the GFP main when an air conditioning compressor fails. In the past it tripped when a maintenance man was changing a light bulb and shorted wires together. I am told that they have adjusted the setting of the GFP breaker to it's maximum allowed setting. Any advice on correcting this problem?
thank you,
![]()
I have a problem with a GFP 1600amp 277/480v service that keeps tripping the GFP main when an air conditioning compressor fails. In the past it tripped when a maintenance man was changing a light bulb and shorted wires together.
That is odd, as a light bulb is usually 120 volt and the 480 volt main GFP would never see a ground fault on 208 or 120 volt circuits.
maybe it was a 277 volt luminaire. Or even 480 volt. Maintenance man may have been doing more than just changing a lamp - especially if he already tried that and it still did not work.
Even shorting the secondary side of a HID ballast would have no effect on the GFP.maybe it was a 277 volt luminaire. Or even 480 volt. Maintenance man may have been doing more than just changing a lamp - especially if he already tried that and it still did not work.