If looking at a one-line and and feeder(about 800') and there is a splice box in the middle would the feeder size be the same on both sides? I would assume it has to be. THe feeder is tageed the same on both sides... Just curious...........:confused:
Thanks.
A 1/0 cu 3ph circuit with an Article 220 calc load of 42A is just fine at 800' (respecting 3% voltage drop).
A #2 cu 3ph circuit with an Article 220 calc load of 75A is probably fine as well at 800' (8.4% VD netting 220V nominal)
Just depends on your circuit specs and Article 220 calc load. VD = SQ RT 3x(KxQ)xIxD/CM & VD = 2x(KxQ)xIxD/CM