erickench
- Brooklyn, NY
Hi Guys, just started reading my book titled "Stallcups Electrical Calculations Simplified". I came across a calculation procedure which Stallcup did not complete. Here is the problem:
What is the load for 40 duplex receptacles used for continuous and 40 duplex receptacles used for noncontinuous duty in illustration 1-6(a)?
The procedure that Stallcup used was this:
Continuous duty load: 180VA x 40 x 125% = 9000VA
Noncontinuous duty load: 180VA x 40 = 7200VA
In applying the demand factors of NEC Table 220.44 Stallcup applies the 100% demand factor to the noncontinuous loads. See the problem? We usually only apply the 125% when the demand factor is 100%. If I were calculating this load I would apply the 100% to the first 9000VA of continuous load and then add on 1000VA to make it 10000VA and to the remaining VA I would apply the 50% demand factor which in this case would be noncontinuous load as it should be. Thus we have
9000 + 1000 + (7200 - 1000) x 50% = 13100VA
The only problem now is what would happen if the continuous load went over 10000VA? How do we bring ourselves to apply both a 50% demand factor and 125% to the same quantity of VAs? Opinions gentlemen!