does a slab need to be grounded for a residential addition? can i get a code reference?the existing service is already grounded and far from the new addition.
the GC had a slab inspection today , He called me , saying that the inspector said that the slab needs to be grounded ....?? is it in the NEC ? or what code?
It is not the slabs or footers that are being grounded. It is the services that are being grounded using the UFER method. The old service is already grounded and needs nothing more. No UFER grounding is required for the addition. A new service being built on an old house also does not require UFER grounding.
250.50 Grounding Electrode System. All grounding electrodes
as described in 250.52(A)(1) through (A)(7) that are
present at each building or structure served shall be bonded
together to form the grounding electrode system......
Slabs never qualify as a uffer.
However, if the footings of the addition contain 20' or more of 1/2" or larger rebar connected together than you must connect it to the service.
250.52(A)(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.) of concrete, located horizontally near the bottom or vertically, and within that portion of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (? in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means. Where multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system.
Slabs never qualify as a uffer.
However, if the footings of the addition contain 20' or more of 1/2" or larger rebar connected together than you must connect it to the service.
I tend to agree with this, except for a little shakiness on the last point, depending on the code cycle in force. I agree with you, and haven't had an issue with '05 and prior cycles here.It is not the slabs or footers that are being grounded. It is the services that are being grounded using the UFER method. The old service is already grounded and needs nothing more. No UFER grounding is required for the addition. A new service being built on an old house also does not require UFER grounding.
The requirement is for service installations, not concrete installations. It's illogical to say that an existing service needs a new electrode just because something that qualifies as one is being built somewhere else on the property.However, if the footings of the addition contain 20' or more of 1/2" or larger rebar connected together than you must connect it to the service.
Iwire, that's why I stressed checking the latest code edit.
250.50 exception says there's no need to connect the rebar if the rebar is not accessible.
The 250.52 section I cited sure looks to me as if every slab that's in contact with the ground can be used- there's no depth requirement at all. Just give me a 4-1/2" chunk of concrete that has either rebar, or a copper wire in it, and you're good to go.
I think we need to re-open the entire topic of 'what is a Ufer.'
I wanted add that any electrode available is supposed to be connected to the service. So if they create one (I.E. the example above) you must use it.
Since when does a slab with rebar qualify as a CEE?
Not in my neck of the woods.
The requirement is for service installations, not concrete installations. It's illogical to say that an existing service needs a new electrode just because something that qualifies as one is being built somewhere else on the property.
250.1 Scope. This article covers general requirements for
grounding and bonding of electrical installations, and the
specific requirements in (1) through (6).
(1) Systems, circuits, and equipment required, permitted,
or not permitted to be grounded
(2) Circuit conductor to be grounded on grounded systems
(3) Location of grounding connections
(4) Types and sizes of grounding and bonding conductors
and electrodes
(5) Methods of grounding and bonding
(6) Conditions under which guards, isolation, or insulation
may be substituted for grounding
does a slab need to be grounded for a residential addition? can i get a code reference?the existing service is already grounded and far from the new addition.
.
Larry you will have to show me the code section that limits 250.52 to new services.
Article 250s scope has nothing at all to do with services.
If you add electrodes they must be connected.
Of course maybe the the EI might let you call it an 'Auxiliary Grounding Electrode' and connect it too an EGC.<JK>
A concrete encased electrode has been required since the 2005 NEC see 250.52(A)(3). The language is for reinforcing located in a footing. A slab does not have a footing. Having said that, using the reinforcing steel in a footing would be nearly the same (for a ground) as in a footing.
Read the language and discuss with your AHJ.
We just had a similar case where grounding was required and no reinforcing steel was present. 680.26(B)(2) using the alternate means.does a slab need to be grounded for a residential addition? can i get a code reference?the existing service is already grounded and far from the new addition.