I have a client that contracts us to perform fire alarm test and inspections. When we document an obvious deficiency that was in place from the original installation, they tell us it's not a problem becuase he AHJ approved it.
Here's a small example: smoke detector in an electrical room, mounted on the wall, 16' AFF. The ceiling height is 30'. If it was installed like that and approved, we leave it alone, but document it.
I have objected quietly, but, that's how its being done.
Your thoughts?? (again, I notify the owner in writing of what was found)