- Chapel Hill, NC
- Retired Electrical Contractor
Thanks to Speedskater, I found the thread I deleted in a cached version.  I am now attempting to repost the thread.
(334.15)
__________________________________________________ __________
Submitter: Mike Holt, Mike Holt Enterprises
Recommendation: Revise text to read:
334.15 Exposed Work. In exposed work, except as provided in 300.11(A), cable shall be installed as specified in 334.15(A) through (C).
(A) Remain unchanged.
(B) Remain unchanged.
(C) In Unfinished Basements and Crawl Spaces . Where cable is run at angels with joists in unfinished basements and crawl spaces , it shall be permissible to secure cables not smaller than two 6 AWG or three 8 AWG conductors directly to the lower edges of the joists. Smaller cables shall be run either through bored holes in joists or on running boards. NM cable used on a wall of an unfinished basement shall be permitted to be installed in a listed conduit or tubing. Conduit or tubing shall utilize a nonmetallic bushing or adapter at the point the cable enters the raceway. Metal conduit and tubings and metal outlet boxes shall be grounded.
Substantiation: The code differentiates between an unfinished basement in different areas of the code, such as in 210.8(A). This code section, however, does not give any direction as to the requirements for a crawl space. Because the same dangers exist in both unfinished basements and crawl spaces, this subsection should be changed to include both locations.
Panel Meeting Action: Accept
Number Eligible to Vote: 14
Ballot Results: Affirmative: 13 Negative: 1
Explanation of Negative:
BROWN, H.: We disagree with the panel action to accept this proposal.
This proposal will allow for cables not smaller than two 6 AWG or three 8 AWG conductors to become fastened directly to the lower edges of joists (in a crawl space). A “crawl space” is not defined in the code. Without placing “height restrictions” or defining a “crawl space” this provision will quickly become a safety issue.
For example: A crawl space may exist beneath a building on a conventional foundation. An individual would have to navigate under surface mounted wiring, (possibly in a “tight” space), while attempting to move around under the building. The individual could “snag” the wiring, and pull it away from its fastening. “Tight spaces” are already an impediment to performing work. Surface mounted cables should not be located in these types of spaces. Without defining “crawl space”, there are no guidelines or restrictions for allowing a lessening of the current rules. The existing installation requirements
provide that the cables must pass through bored holes. This has been an accepted practice for many years, as it provides for a safe installation of the product. Are we becoming too lazy to bore holes to protect our wiring method? Let’s continue to give the consumer, the service technicians, and everyone else (pest control, etc.) a safe and efficient electrical installation.
			Bullheimer said:Would somebody mind reading page 297 of the 2011 handbook and explain to me what this means as far as stapling cables to the bottoms of floor joists in a crawl space? EXHIBIT 300.2
iT seems to me they are prohibiting stapling to the bottoms of floor joists generally. only if there is a guard strip next to them or they are on a board. did something seriously change things?
Hotwire1955 said:Same as it was in 2008 code 334.15 (C)
Bullheimer said:that explains it. i dont read anything cept Handbooks and Comic books. if it aint got pictures, then forget it.
So, now that we have established that it is wrong to staple 12-2 to bottoms of floor joists, IS ANYBODY OUT THERE ACTUALLY BEEN COMPLYING WITH THIS?
This sounds like the biggest PANT LOAD i've ever heard of. i have not stopped and i have never been called on it, ever. have you? i think this is just absolutely absurd. It just can't be that the only reason i havent been nailed on this is because not even one single inspector went under the house??? WHAT possible reason could this actually serve? Yes another code rule that has no concept of reality. Really? drill holes in the floor joists? you KNOW that AINT gonna happen. sorry, i know nobody here wrote the codebook.
Hotwire1955 said:(Crawl spaces) was added in 2008 code
Stew said:Does anyone on here know what caused the codemakers to change this. Where is the hazard in this? Rats doing pullups?
7-58 Log #2399 NEC-P07 Final Action: AcceptInfinity said:Mike Holt wrote the proposal:
(334.15)
Jumper said:VA amended this and deleted the requirement for crawl spaces.