I have seen industrial contol panels with 800A feeders.
What does amperage have to do with color coding for voltage?
I misread your post.
You and Don can pull all black wires for a safer install! Heck, invite Iwire too!
Two bosses and an engineer...I don't see how anything would get doneNow there would be a wire pulling team![]()
Two bosses and an engineer...I don't see how anything would get done![]()
Other than meetings right?Two bosses and an engineer...I don't see how anything would get done![]()
LOL
The project would be doomed. :grin:
Other than meetings right?![]()
I agree that odd colors are permitted, and it's probably not a safety issue.
But I completely agree with the original poster that this is a workmanship issue. What I look for in an employee, among other things, is a sense of professionalism. A panel that has the conductors routed neatly, with an obvious color code, looks sharp. One with random colors looks shoddy. I'd start to question the work ethic of a journeyman who said to me, "Ah, man. It's just colors! Chill." Just my opinion.
I agree with the workmanship issue making things neat and orderly is a top priority of mine. But if there is a job here to be done and all i have is Black wire for the ungrounded conductor that is what i will use. like the one post said Electricity does not know the differance in color of the wire.
I reckon I'd do the same thing. I guess I was thinking more along the lines of new construction where you had the time to plan out the job rather than a service call where you're just trying to fix the darn thing and get it running again.
There are not enough (basic) colors to have a separate color code for every possible voltage system that may exist. How would you identify the following systems and phases with colors alone if you had all of these in one facility? Or use same color code on multiple facilities without ever using same color on more than one system. Green is alread lost to EGC, white and gray are lost to grounded conductors that leaves only about 8 or so basic colors for 18 different ungrounded conductors just in this list alone. How do you identify 7 different grounded conductors in this list with only white and gray?
120/240 single phase Black, Red, White
120/240 three phase Black, Red, Blue, White, but sub high leg with Orange
120/208 three phase Black, Red, Blue, White
277/480 three phase Brown, Orange, Yellow, Grey
347/600 three phase Brown, Orange, Yellow, Grey
240 three phase with grounded phase Grounded phase used as neutral?
480 three phase with grounded phase
The colors that have become pretty much the standard for 120/208 and 277/480 are fine but one still needs to verify what they have before just looking at a the colors and assuming. That is part of why the ID method needs posted at each panelboard. Not in NEC but many industrial places have panel voltage posted in obvious place on outside of panels or on outside of discnnects or other enclosures like a machine control panel.
There is no neutral in this system. A three phase corner grounded system has only 3 circuit conductors. You will have 480 phase to phase for all 3 phases, you will have 480 phase to ground for 2 of the phases, and you will have 0 to ground for the grounded phase.I don't follow your reference to grounded phase. A neutral is pulled from transformer windings, middle point for wye, halfway between 2 phases for delta, hence the high leg. Can you give me more detail?
You are assuming that all grounded systems are wye sources (i.e. an X0 terminal is available). It is possible to have delta connected sources in both ungrounded and grounded configurations.We learn something every day. All 480 systems I've worked with were 480 phase to phase & 277 phase to neutral or phase to ground. Seems if you had 480 phase to ground, you would have 832 phase to phase.
the NEC requires it to be white but it is not a neutral.
Grounded Conductor. A system or circuit conductor that is intentionally grounded.
Neutral Conductor. The conductor connected to the neutral point of a system that is intended to carry current under normal conditions.
Neutral Point. The common point on a wye-connection in a polyphase system or midpoint on a single-phase, 3-wire system, or midpoint of a single-phase portion of a 3-phase delta system, or a midpoint of a 3-wire, direct-current system.
FPN: At the neutral point of the system, the vectorial sum of the nominal voltages from all other phases within the system that utilize the neutral, with respect to the neutral point, is zero potential.