Panel Meeting Action: Accept in Principle 
Revise 250.68(C) in ROP draft to read as follows: 
   “(C) Metallic Water Pipe and Structural Metal. Grounding electrode 
conductors and bonding jumpers shall be permitted to be connected at the 
following locations and be used to extend the connection to an electrode(s): 
   (1) Interior metal water piping located not more than 1.52 m (5 ft) from the 
point of entrance to the building shall be permitted to be used as a conductor to 
interconnect electrodes that are part of the grounding electrode system. 
Exception: In industrial, commercial, and institutional buildings or structures 
if conditions of maintenance and supervision ensure that only qualified persons 
service the installation, interior metal water piping located more than 1.52 m 
(5 ft) from the point of entrance to the building shall be permitted as a bonding 
conductor to interconnect electrodes that are part of the grounding electrode 
system, or as a grounding electrode conductor, provided that the entire length, 
other than short sections passing perpendicularly through walls, floors, or 
ceilings, of the interior metal water pipe that is being used for the conductor is 
exposed. 
(2) The structural metal frame of a building that is directly connected to a 
grounding electrode as specified in 250.52(A)(2) or 250.68(C)(2)(a), (b) or (c) 
shall be permitted as a bonding conductor to interconnect electrodes that are 
part of the grounding electrode system, or as a grounding electrode conductor. 
a. By connecting the structural metal frame to the reinforcing bars of a 
concrete-encased electrode as provided in 250.52(A)(3) or ground ring as 
provided in 250.52(A)(4) 
   b. By bonding the structural metal frame to one or more of the grounding 
electrodes as defined in 250.52(A)(5) or (A)(7) that comply with 250.53(A)(2) 
   c. By other approved means of establishing a connection to earth” 
   Revise recommended text for 250.64(C) from this comment to read as 
follows: 
   “250.64(C) Continuous. Except as provided in 250.30(A)(5), (A)(6), 
250.30(B)(1) and 250.68(C), grounding electrode conductor(s) shall be 
installed in one continuous length without a splice or joint. If necessary, splices 
or connections shall be made as permitted in (1) through (4): 
   (1) Splicing of the wire-type grounding electrode conductor shall be 
permitted only by irreversible compression-type connectors listed as grounding 
and bonding equipment or by the exothermic welding process. 
   (2) Sections of busbars shall be permitted to be connected together to form a 
grounding electrode conductor. 
   (3) Bolted, riveted, or welded connections of structural metal frames of 
buildings or structures. 
   (4) Threaded, welded, brazed, soldered or bolted-flange connections of metal 
water piping.” 
Panel Statement: The revised text for 250.68(C) incorporates Comments 
5-130 and 5-131 with editorial revisions made for clarity. The recommended 
text for 250.64(C) was accepted with changing the term “required” to 
necessary”.  
Number Eligible to Vote: 16 
Ballot Results: Affirmative: 16