450.9 Ventilation.
The ventilation shall be adequate to dispose of the transformer full-load losses without creating a temperature rise that is in excess of the transformer rating.
FPN No. 1: See ANSI/IEEE C57.12.00-1993, General Requirements for Liquid-Immersed Distribution, Power, and Regulating Transformers, and ANSI/IEEE C57.12.01-1989, General Requirements for Dry-Type Distribution and Power Transformers.
FPN No. 2: Additional losses may occur in some transformers where nonsinusoidal currents are present, resulting in increased heat in the transformer above its rating. See ANSI/IEEE C57.110-1993, Recommended Practice for Establishing Transformer Capability When Supplying Nonsinusoidal Load Currents, where transformers are utilized with nonlinear loads.
Transformers with ventilating openings shall be installed so that the ventilating openings are not blocked by walls or other obstructions. The required clearances shall be clearly marked on the transformer.