Thanks, I meant to say short circuit. I don't know why I was thinking arc.
So is the following correct? 75 KVA = 75,000/240 volts = 312.5 amps. 312.5/.05 = 6,250 short circuit current
Is that for single phase or three phase.
I get 4,009 on a three phase transformer using the Bussman point to point calculations.
Is that for single phase or three phase.
I get 4,009 on a three phase transformer using the Bussman point to point calculations.
Tim,
Is that a single phase transformer?
Is the result correct in my formula with the parameters that I used?
I am trying to see if I interpreted it correctly and that I wrote the excel formula right.