calculating arc fault current

Status
Not open for further replies.

Ken 6789

Senior Member
How do you calculate arc fault current of a transformer? I believe KVA and transformer impedance are factors in calculation, but not sure how it's done. Would someone give an example? Thanks.
 
If you are asking about the short circuit current, it is the full load amps divided by the impedance (in decimal form, 5% =0.05). This will give you a "infinite bus" value which is the worst case.
 
Thanks, I meant to say short circuit. I don't know why I was thinking arc.

So is the following correct? 75 KVA = 75,000/240 volts = 312.5 amps. 312.5/.05 = 6,250 short circuit current
 
Last edited:
Do not use the infinite bus method to determine the only short circuit current which will be used when performing an arc flash calculation.
 
Thanks, I meant to say short circuit. I don't know why I was thinking arc.

So is the following correct? 75 KVA = 75,000/240 volts = 312.5 amps. 312.5/.05 = 6,250 short circuit current

Yes. That's a conservative estimate, assuming there aren't any large motors that would contribute a lot.
 
Is that for single phase or three phase.

I get 4,009 on a three phase transformer using the Bussman point to point calculations.

AIC.jpg
 
Is that for single phase or three phase.

I get 4,009 on a three phase transformer using the Bussman point to point calculations.

AIC.jpg

FWIW,
With the current generation of energy efficient transformers, 5% is a relatively high impedance for a 75kVA 3-ph dry type, and it is extremely high for a utility supplied liquid filled unit (Xcel Energy recommends using 1.6%Z)
 
Is the result correct in my formula with the parameters that I used?

I am trying to see if I interpreted it correctly and that I wrote the excel formula right.
 
Is the result correct in my formula with the parameters that I used?

I am trying to see if I interpreted it correctly and that I wrote the excel formula right.


If we assume its a 240V, three phase system, with 5% Z: I get 3608 Amps.

75,000/(240*1.73)= 180 amps.

180/.05 = 3608
 
The original posters calculation left out the 1.73 so I assume we are talking about a single phase transformer.
 