Guyute
Member
- Location
- Ft Collins, CO
I have a 400 amp service with a 400amp em disconnect for the genset with an ATS. There is no breaker on the genset, and the neutral is bonded at the genset. Do I bond and ground the 400amp em disconnect to the ufer, water, etc or is the ground rod and ufer at the genset suffiecient for my main bond. My big confusion is if in a back up power situation doesn't the 400 amp em disconnect become the main means of disconnect and a seperately derived system. If this is the case then I would need to have my main bonding electrode at the em disconnect sized according to 250.66. I also have to have an equipment bond between the generator and the disconnect. Any thoughts.